# CHT v2 steady: coolant outlet ΔT ~7.5× higher than energy balance (2280 W in, ~17 kW out)

**URL:** <https://www.simscale.com/forum/t/cht-v2-steady-coolant-outlet-t-7-5x-higher-than-energy-balance-2280-w-in-17-kw-out/101550>\
**Category:** Project Support\
**Created:** [November 29, 2026, 5:32pm UTC](https://www.simscale.com/forum/t/cht-v2-steady-coolant-outlet-t-7-5x-higher-than-energy-balance-2280-w-in-17-kw-out/101550 "2026-11-29T17:32:22Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![jaylabhade19](https://www.simscale.com/forum/letter_avatar/jaylabhade19/32/6_449c533f586939b6e5f246632a46421f.png) [@jaylabhade19](https://www.simscale.com/forum/u/jaylabhade19)\
**Post date:** [November 29, 2026, 5:32pm UTC](https://www.simscale.com/forum/t/cht-v2-steady-coolant-outlet-t-7-5x-higher-than-energy-balance-2280-w-in-17-kw-out/101550/1 "2026-11-29T17:32:22Z")

</div>

Hi all, I’m running a steady CHT v2 study of a generic e-machine with a helical water-glycol jacket. Project is public: **“MGU-K CHT study, rotor-bearing heat path”**.

**Setup**  
– Fluid: ρ 1060 kg/m³, cp 3400 J/kgK, ν 3.302e-6 m²/s, Pr 29.75 (k-ω SST, incompressible, steady)  
– Inlet: mass flow 0.1413 kg/s, 40 °C. Outlet: pressure 0 Pa  
– 4 absolute power sources in solids: 2000 / 200 / 40 / 40 W (total 2280 W). All other external walls adiabatic.

**Expected:** T\_out = 40 + 2280 / (0.1413 · 3400) = **44.7 °C**  
**Result:** T\_out = **76 °C** (ΔT ≈ 36 K, i.e. ≈ 17 kW absorbed by the coolant)

**What I already checked**

1. Power sources in downloaded case (fvOptions): `volumeMode absolute`, one cellZone each (region2/3/6/7). Coolant is region4, no source there.
2. Mass flow confirmed by area-averaged inlet/outlet velocity (2.66 / 2.73 m/s through Ø8 mm).
3. Same result on two meshes (14.4 M and 4.1 M cells), with and without non-orthogonal correctors.
4. Changing solid cp (450 → 4500) gives an identical T\_out curve.
5. Initial T = 40 °C, inlet T = 40 °C verified.
6. `constant/region4/transportProperties` contains nu, rhoRef, Pr, Prt — **no Cp**.
7. Solver log: continuity errors “sum local” ≈ 0.01 per iteration, T residual stalls at ~8e-5.

Since the coolant cannot absorb more than the 2280 W injected in steady state, this looks like the fluid ρ·cp not being applied as expected in the solid–fluid coupling. Is there a setting I’m missing, or is this a known issue? Thanks!